Hey guys, just got a call that the reheat coils for a job we did are not working (when thermostat set higher, heaters not kicking in). Now these are five 8" titus single duct boxes with 2kw heaters. The heating cfm's range from 90-120cfm. I think that they are heating the air too high and tripping a high limit cutout. I did the calcs and the 90 cfm minimum box would heat the air to 122 deg, when I want it around 95. I am thinking that they can adjust the minimum damper position for heating mode. Is this correct? I will bump the minimum up to around 200 cfm.
This of course after we check that the thermostats are hooked up and everything electrically is in order.
Am I right?
This of course after we check that the thermostats are hooked up and everything electrically is in order.
Am I right?