Hello, I have a high-rise art school project that I am designing using a four pipe Fan Coil Unit with primary air system from a Dedicated Outdoor Air System (100% outdoor air unit w Energy Recovery wheel)
To meet LEED Silver, a point requires CO2 sensors in high density occupant spaces. The plan would be for the CO2 sensor to control a modulating damper (like VAV box). The supply fan VFD shall be controlled on the Static Pressure of the supply ductwork. As dampers close, the SP increases, the Supply Fan (SF) VFD slows, and fan energy is saved. (My goal is maximum efficiency, for max LEED points).
The Return Fan (RF) of the ERU would track the SF, so as the SF speed reduces so will the RF. The RF exhausts the bathroom that have a constant volume exhaust of 50 cfm per ASHRAE 62-2007. So as the RF speed slows, it will reduce less than code required exhaust from the bathrooms.
How can I resolve this?
1. Provide exhaust boxes, modulating dampers on the RF systems, and let the RF be controlled on RF SP, instead of tracking the SF. I would prefer not to do this, as it will require VAV boxes on the return of the art classroom etc. This would work, but now I have to add return boxes to every space in a high rise? That can get expensive and require space that is at a premium.
2. Double the exhaust rates required, so when the RF goes to 50% speed, the code required cfm is still exhausted.
This may work, but doesn't feel very energy efficient. Unless you come from the school of providing 10 Air Changes per Hour of exhaust air from the bathrooms is good practice, because that would require over 100 cfm of exhaust, so this system would work well with this control sequence.
So I was wondering if there was another way, other than additional boxes, or guess engineering.
Thank you
knowledge is power
To meet LEED Silver, a point requires CO2 sensors in high density occupant spaces. The plan would be for the CO2 sensor to control a modulating damper (like VAV box). The supply fan VFD shall be controlled on the Static Pressure of the supply ductwork. As dampers close, the SP increases, the Supply Fan (SF) VFD slows, and fan energy is saved. (My goal is maximum efficiency, for max LEED points).
The Return Fan (RF) of the ERU would track the SF, so as the SF speed reduces so will the RF. The RF exhausts the bathroom that have a constant volume exhaust of 50 cfm per ASHRAE 62-2007. So as the RF speed slows, it will reduce less than code required exhaust from the bathrooms.
How can I resolve this?
1. Provide exhaust boxes, modulating dampers on the RF systems, and let the RF be controlled on RF SP, instead of tracking the SF. I would prefer not to do this, as it will require VAV boxes on the return of the art classroom etc. This would work, but now I have to add return boxes to every space in a high rise? That can get expensive and require space that is at a premium.
2. Double the exhaust rates required, so when the RF goes to 50% speed, the code required cfm is still exhausted.
This may work, but doesn't feel very energy efficient. Unless you come from the school of providing 10 Air Changes per Hour of exhaust air from the bathrooms is good practice, because that would require over 100 cfm of exhaust, so this system would work well with this control sequence.
So I was wondering if there was another way, other than additional boxes, or guess engineering.
Thank you