remp
Mechanical
- Sep 15, 2003
- 224
Im constructing a pressure independent VAV system in a high rise building. The air handling unit fans ramp up and down on a vatriable speed drive (freq. inverter) to maintain a constant pressure in the supply duct through a pressure sensor about 2/3 the way down the duct.
At present I have supply air temperature reset based on the zone demanding the most cooling, so if all VAV boxes are say 60% closed the supply air temperature will reset above the design temperature. This will eventually cause the boxes to open more and the fan to ramp up. This method has lower chilled water gennerating costs.
The consultant on the job wants to delete the pressure sensor from the system because its a pressure independent system. ok he has a point here. But he wants to control the supply fan speed based on the box that requires the most cooling by using "OPEN LOOP CONTROL", if the box requiring the most cooling is just off its max position slow down the fan a little. Again after another 5 minutes watch if and VAV box is not preforming then ramp up the fan a little.
He want to do this for enegry saving. With this method there will be no supply temperature reset so less energy savings on the chiller. The consultant reckons there will be more savings on fan power.
What are you thoughts on this OPEN LOOP CONTROL?
Im in Australia, someone from Trane here told me this is how its done in US. Is this true?
At present I have supply air temperature reset based on the zone demanding the most cooling, so if all VAV boxes are say 60% closed the supply air temperature will reset above the design temperature. This will eventually cause the boxes to open more and the fan to ramp up. This method has lower chilled water gennerating costs.
The consultant on the job wants to delete the pressure sensor from the system because its a pressure independent system. ok he has a point here. But he wants to control the supply fan speed based on the box that requires the most cooling by using "OPEN LOOP CONTROL", if the box requiring the most cooling is just off its max position slow down the fan a little. Again after another 5 minutes watch if and VAV box is not preforming then ramp up the fan a little.
He want to do this for enegry saving. With this method there will be no supply temperature reset so less energy savings on the chiller. The consultant reckons there will be more savings on fan power.
What are you thoughts on this OPEN LOOP CONTROL?
Im in Australia, someone from Trane here told me this is how its done in US. Is this true?