Hi all, HVAC consultant here seeking some wisdom...
I have been mandated by my client to determine the annual cost savings associated with retrofitting air handling units serving a VAV system from inlet guide vanes to VFD's.
The current method of controlling the airflow with the inlet guide vanes is by maintaining static pressure setpoint at the fan discharge.
From what I am putting together at this point, I fail to see any operating savings at all within the throttling range of the inlet guide vanes. Since the VFD will also be controlled to maintain the static pressure setpoint, at any operating point, both the static pressure and airflow will be the same as with the inlet guide vanes, the system curve does not change, therefore BHP will also be the same.
At low airflow conditions, I can see that a VFD could achieve some savings. But my problem here is to determine what is the point where the inlet vanes are fully tilted and can no longer "help" the fan. I have tried to model how the fan curve changes with the throttling of the inlet guide vanes but I have failed with both the Greeheck (CAPS) and Penn Ventilator (FanSizer) software, they do not provide this capability.
For reference, the units are equipped with 16,000 cfm fans, 20-HP motors, and I am estimating design static pressure as 4" WG.
I've looked at this reference from the Trane Engineer's newsletter, you might want to check it out.
I've also found this very un-scientific energy savings calculator that claims a kind of "fudge factor" of 62% for inlet guide vanes to 28% for VFD's.
Any thoughts are very welcome...Thanks !!!
I have been mandated by my client to determine the annual cost savings associated with retrofitting air handling units serving a VAV system from inlet guide vanes to VFD's.
The current method of controlling the airflow with the inlet guide vanes is by maintaining static pressure setpoint at the fan discharge.
From what I am putting together at this point, I fail to see any operating savings at all within the throttling range of the inlet guide vanes. Since the VFD will also be controlled to maintain the static pressure setpoint, at any operating point, both the static pressure and airflow will be the same as with the inlet guide vanes, the system curve does not change, therefore BHP will also be the same.
At low airflow conditions, I can see that a VFD could achieve some savings. But my problem here is to determine what is the point where the inlet vanes are fully tilted and can no longer "help" the fan. I have tried to model how the fan curve changes with the throttling of the inlet guide vanes but I have failed with both the Greeheck (CAPS) and Penn Ventilator (FanSizer) software, they do not provide this capability.
For reference, the units are equipped with 16,000 cfm fans, 20-HP motors, and I am estimating design static pressure as 4" WG.
I've looked at this reference from the Trane Engineer's newsletter, you might want to check it out.
I've also found this very un-scientific energy savings calculator that claims a kind of "fudge factor" of 62% for inlet guide vanes to 28% for VFD's.
Any thoughts are very welcome...Thanks !!!