Where does it state there must not be vegetation growing close to API 650 Storage Tanks. I know there shouldn't be but I need to show someone it is an actual requirement.
 
Replies continue below

Recommended for you

API 653 (tank inspection standard) recommends the tank foundation be inspected for cracks/deterioration (Section 4.5) which is typically where vegetation will grow. Additionally, the In-Service Inspection Checklist seen in Appendix C contains a housekeeping line item to inspect for trash, vegetation, and inflammables.

Vegetation is typically found in the secondary containment (dike area around a tank); if the product stored requires secondary containment vegetation may be a warning sign that the containment needs repair.
 
Define "close to".

A cm, a m, 10m??

I think this one just goes under the code of common sense...

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
LittleInch: You would think common sense wouldn't you?