Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Vehicle Barriers 2

Status
Not open for further replies.

Taro

Structural
Nov 29, 2000
713
A project I am working on includes a few guard shacks that are protected from vehicle collision by cantilevered cast-in-place concrete walls. The design criteria for the barrier walls is to be AASHTO Roadside Design Guide 3. As a building engineer, I do not have this reference. Can someone summarize the design loads for me?
 
Replies continue below

Recommended for you

The basic collision load for AASHTO vehicles is 10 Kips applied at the top of the barrier height (for most cases about 3' above roadway). There are several distribution diagrams in the official AASHTO Design Guide, but for bridge design of the safety barrier curb we use the 10 kip load. That load is then chased through the barrier and into the bridge slab - it sometimes controls the slab design.

Regards,
Qshake
[pipe]
Eng-Tips Forums:Real Solutions for Real Problems Really Quick.
 
Just a reminder that the 10 kip load is distributed over a 5' width (2 kips/ft.)

 