Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

vent design

Status
Not open for further replies.

jeanfrancois3869

Industrial
Joined
Feb 21, 2010
Messages
14
Location
FR
Hi,

I'm working about the integrated counting system design and I wonder how to design my vents for gas and liquid.
Norsok P-001 speaks about maximal velocities in vents equal to mach 0,5, but it creates very large velocities. In practice, are there sizes which are preconized?
 
Just the std pipe and valve sizes. It depends on what you're venting, why you're venting and how much time you have to do it. Venting a high point, a strainer trap bowl, or a prover tube on a meter system when starting up or changing products shouldn't be needing much more than a 1/2 ", maybe a 1" in some places, possibly a 2" vent, if venting off a large main line. Anything more than that, you're going to overspeed a turbine, or create some serious disturbence nearby, not something you want to do on a meter system. Are you venting for some emergency situation, or just normal startup, purging air from lines, clearing interfaces and venting to drains from normal operation scenarios?

**********************
"The problem isn't working out the equation,
its finding the answer to the real question." BigInch
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top