Ventilation for locker rooms, 62.1-2007, BOCA

Status
Not open for further replies.

NEplantengineer

Mechanical
Joined
Mar 8, 2004
Messages
14
Location
US
Hi Folks,

Wondering if anyone has an old copy of the BOCA 1987 mechanical code. If so, I was wondering what it states as the min ventilation rate for locker rooms/areas. I'm looking at an old basis of design where it is stated that the rate is 35 cfm per person per the 1987 Code. I have the 1993 BOCA version which says 0.5 cfm/ft2.

Also wondering if anyone has an opinion to what folks typically use (in ASHRAE 62.1-2007) for the People outdoor rate (Rp) and Area outdoor rate (Ra) for a locker room? Or do folks normally just skip to section 6.4 and use the 0.5 cfm/ft2 for exhaust.
 
For Part 1 anyways, BOCA 87 does state 35 cfm per person in a locker room, and allows no more than 85% of the ventilating air to be recirculated.
 
Chas - Thanks for the reply. Very interesting that BOCA 87 says no more than 85% can be recirc'd. The BOD that I have says none shall be recirc'd. Just another mistake, I find them all the time!
Thanks again.
 
No recirculation is not necessarily a mistake. A lot of these spaces can meet ventilation requirements with draw-through, depending on heat load, without fan coils or FPT boxes... The 85% is a max allowable, not a min requirement...

CB
 