ChrisConley
Mechanical
- May 13, 2002
- 975
Hello all,
I have a repair garage that requires ventilation to meet code. The code requirements for a repair garage are 1.5 cfm/ft2 as per ASHRAE 62.
This works out to 11,000 cfm of OA and a pretty large make-up air handler for the size of the building (around 7300 ft2)
ASHRAE 62, and the Canadian National Building Code, do allow for natural ventilation of spaces where the occupancy is less than one person per 430 ft2, which is the case for the repair garage in question.
Again, ASHRAE 62 states that if operable openings with a total area of or 4% of the floor space are provide the space can be considered naturally ventilated (I'm summarizing). The large overhead door will have an area of over 8% of the floor space so we should have no problems with that requirement.
The ASHRAE Standard's main concern seems to be controlling humidity (which is not a concern where I am) and not dealing with cold temperatures.
My question is (sorry it took so long to get here) is that although it seems to meet code, I'm uncomfortable providing natural ventilation only for a repair garage. I know that during winter (-40deg) no mechanic will open the garage door to ensure their space is well ventilated.
Has anyone else run into this situation? What has anyone else done to ventilate a repair garage?
I have a repair garage that requires ventilation to meet code. The code requirements for a repair garage are 1.5 cfm/ft2 as per ASHRAE 62.
This works out to 11,000 cfm of OA and a pretty large make-up air handler for the size of the building (around 7300 ft2)
ASHRAE 62, and the Canadian National Building Code, do allow for natural ventilation of spaces where the occupancy is less than one person per 430 ft2, which is the case for the repair garage in question.
Again, ASHRAE 62 states that if operable openings with a total area of or 4% of the floor space are provide the space can be considered naturally ventilated (I'm summarizing). The large overhead door will have an area of over 8% of the floor space so we should have no problems with that requirement.
The ASHRAE Standard's main concern seems to be controlling humidity (which is not a concern where I am) and not dealing with cold temperatures.
My question is (sorry it took so long to get here) is that although it seems to meet code, I'm uncomfortable providing natural ventilation only for a repair garage. I know that during winter (-40deg) no mechanic will open the garage door to ensure their space is well ventilated.
Has anyone else run into this situation? What has anyone else done to ventilate a repair garage?