koshyeng
Chemical
- Nov 12, 2007
- 103
I need to size a PVRV for an acetone tank( low pressure storage tank) in our facility which will have a weak roof to shell attachment. API 2000 doesn't show any equations for this case except inbreathing and outbreathing values.
My tank capacity will be 20,000 gal and since Acetone flash point is below 100 deg F, I came up with this numbers from API 2000.
Inbreathing = (5.6 + 500)SCFH of air. Liquid movement plus thermal effect.
Outbreathing = ( 12+ 500) SCFH of Air.
Emergency venting requirement is not required as it has weak roof to shell attachment.
Appreciate your comments on these values.
Thank You
Koshy