Vertical reinforcement

Status
Not open for further replies.

rbhall

Civil/Environmental
Nov 24, 2011
21
Drawings show a 12" thick concrete wall indicating double #5 at 12"oc. The contractor installed the inside #5 bars offset from the outside #5 bars. I have always been taught to install the bars directly across from each other. The drawing does not have a top view of the wall therefore I have no way to verify if the bars are required to be directly across from each other. Does anyone know of a requirement for having the bars directly across from each other?
 
Replies continue below

Recommended for you

There is no requirement for inside and outside bars to align, and no real reason to do it.
 
Status