A query came through our USA sales channel asking about the use of a VFD on a Vertical Turbine Pump, 100Hp rated (little else at this stage).
I recalled an application I did with one about 8 years or so ago and one of the main issues with using one with a VFD was:
1) The acceleration time had to be very quick (this was a 160kW rated pump and we needed an accel time of about 10 secs) to ensure the bearings were quickly lubricated. The resulting starting duty demanded a VFD with a high overload.
2) Stopping the pump resulted in the 'backflow' of the pumped medium causing a certain level of regeneration (brake resistors fitting).
The question is, am I generalising with Vertical Turbine pumps in thinking they will all have similar performance requirements or is this about right? If the feeling is that all VTP's are different, then I will go back and get a lot more details from them.
They wanted to use one of our low dynamic HVAC drives, but I've initially said no, I think they should be looking at a more higher performance 'industrial' drive.
I recalled an application I did with one about 8 years or so ago and one of the main issues with using one with a VFD was:
1) The acceleration time had to be very quick (this was a 160kW rated pump and we needed an accel time of about 10 secs) to ensure the bearings were quickly lubricated. The resulting starting duty demanded a VFD with a high overload.
2) Stopping the pump resulted in the 'backflow' of the pumped medium causing a certain level of regeneration (brake resistors fitting).
The question is, am I generalising with Vertical Turbine pumps in thinking they will all have similar performance requirements or is this about right? If the feeling is that all VTP's are different, then I will go back and get a lot more details from them.
They wanted to use one of our low dynamic HVAC drives, but I've initially said no, I think they should be looking at a more higher performance 'industrial' drive.