Thanks for the replies. To take the discussion further I give some relevant details. we have 3 x 50% (2 running & 1 standby) centrifugal pumps feeding a common header and then individual lines feed the Boilers thru control valve (CV). With the existing set-up, we can not directly transfer the CV controls to the VFD as the inputs could be different for different Boilers. This also means that there can be a case where all the three control valves get closed, the flow requirement becomes nearly zero, the VFD will still run the pp at its min speed, but no flow as the min flow valve will not operate. This further means that we can not altogether get rid of the min flow valve as suggested by 'monaco8774' and have to have some way to protect the pp in the worst case scenario of no flow.
And thanks 'sed2developer' for your thoughts. In our case the pp discharge pr is 19 bar and drum pr is 7 bar, so we may be running at times at less than 40 Hz also. Regarding orifice, I feel it will always allow some amount of water to pass and hence not efficient. I also note that you have mentioned controlling the VFD so as to hold the pp discharge pr constant, this gives us one way of control. Another way is to take the open feedback from the different Drum Level Control Valves and regulate VFD such that at least one valve is held near to 100% opening (say 90%), do you think this can work?
Another issue is, one of the VFD supplier suggested running one pump at full load and the second one to run with VFD? Is this a good idea?
And yes, I still look forward to some idea from someone to overcome the min flow problem with VFD!