Jieve
Mechanical
- Jul 16, 2011
- 131
Hello,
We are working on a conveyor system to be used for educational purposes. The system consists of 7 control cabinets: 1 main for power distribution and e-stop circuits, 5 sub-cabinets, each with Siemens PLCs and 1 motor control center. The first component in the main cabinet is a 3-phase type A 30mA RCD. There are 5x 0.4hp 3-phase (400V, 50Hz) motors controlling the conveyors, and each will be controlled by a Siemens G120 VFD. All motor cables will be shielded and grounded at both motor and VFD. The VFD’s do not have built in filters, and we are not using any externally.
My question is regarding using RCDs with the VFDs. The G120 manual recommends using a single 300mA type B RCD before each VFD. I have done a lot of web research, and there seems to be mixed opinions about this – there is a large number of people who say to leave the RCD’s out because they constantly nuisance trip due to earth leakage currents. To simulate our system, I ran a bench test running a single type A 30mA RCD upstream of 5 of these VFDs running 5x 1hp motors. I varied motor speeds and run a number of tests with no problems.
As I understand it, type A RCD’s will trip on sinusoidal currents with DC offset, and type B RCD’s will also trip on pure DC currents. I want this system to be as safe as possible as students will be using it for PLC programming practice. We are not using braking resistors on any of the VFDs. Here in Germany, 30mA RCDs are required for direct touch protection. I have read that 300mA are allowed when using VFD’s because the harmonics in the rectified signal results in higher frequency fault currents, which are not as dangerous to the cardiovascular system at 30mA as 50Hz AC currents.
My question is then: Would it make sense to add these type B 300mA RCDs before each drive or are they redundant and can we leave them out? Is it correct that the type A 30mA RCD that is feeding the rest of the system would not catch DC earth leakage currents that may potentially cause injury, therefore requiring the installation of the 300mA RCDs, or is this not the case? In one Schneider document I found on VFD’s and RCD compatibility, they recommend 30mA type A RCDs on each drive in a TN-S system (our grounding system), which is different than the Siemens recommendation, and seems redundant if our main RCD doesn’t nuisance trip.
I’d really appreciate any info from anyone with more experience than I in this area. Thanks!!
We are working on a conveyor system to be used for educational purposes. The system consists of 7 control cabinets: 1 main for power distribution and e-stop circuits, 5 sub-cabinets, each with Siemens PLCs and 1 motor control center. The first component in the main cabinet is a 3-phase type A 30mA RCD. There are 5x 0.4hp 3-phase (400V, 50Hz) motors controlling the conveyors, and each will be controlled by a Siemens G120 VFD. All motor cables will be shielded and grounded at both motor and VFD. The VFD’s do not have built in filters, and we are not using any externally.
My question is regarding using RCDs with the VFDs. The G120 manual recommends using a single 300mA type B RCD before each VFD. I have done a lot of web research, and there seems to be mixed opinions about this – there is a large number of people who say to leave the RCD’s out because they constantly nuisance trip due to earth leakage currents. To simulate our system, I ran a bench test running a single type A 30mA RCD upstream of 5 of these VFDs running 5x 1hp motors. I varied motor speeds and run a number of tests with no problems.
As I understand it, type A RCD’s will trip on sinusoidal currents with DC offset, and type B RCD’s will also trip on pure DC currents. I want this system to be as safe as possible as students will be using it for PLC programming practice. We are not using braking resistors on any of the VFDs. Here in Germany, 30mA RCDs are required for direct touch protection. I have read that 300mA are allowed when using VFD’s because the harmonics in the rectified signal results in higher frequency fault currents, which are not as dangerous to the cardiovascular system at 30mA as 50Hz AC currents.
My question is then: Would it make sense to add these type B 300mA RCDs before each drive or are they redundant and can we leave them out? Is it correct that the type A 30mA RCD that is feeding the rest of the system would not catch DC earth leakage currents that may potentially cause injury, therefore requiring the installation of the 300mA RCDs, or is this not the case? In one Schneider document I found on VFD’s and RCD compatibility, they recommend 30mA type A RCDs on each drive in a TN-S system (our grounding system), which is different than the Siemens recommendation, and seems redundant if our main RCD doesn’t nuisance trip.
I’d really appreciate any info from anyone with more experience than I in this area. Thanks!!