VFD CABLE

Status
Not open for further replies.

maziarkh

Electrical
Mar 17, 2012
2
I have a question about maximum cable length between VFD and motor ,MV or LV , is there any table or formula in this regard?

 
Replies continue below

Recommended for you

No table that would be meaningful as a generalization across platforms. Different drive topologies will cause different problems and dictate different strategies to deal with them, which will always affect the maximum length of motor lead cable. The type of cable makes a difference as well. If you have a specific issue and you know the details of what you have to deal with, post it and there are many people here that can offer strategies.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> faq731-376
 
I'm sure jraef's comments are on the money.

Google "Riding The Reflected Wave" for one article on the subject

=====================================
(2B)+(2B)' ?
 
On the other hand ABB sustain that their driver provided with dv/dt filter will present no overshoot at any frequency-no limitation for 600 V cable.
That means the usual criteria of load and short-circuit heating and voltage drop will rule the supply cable choice.
See:
 