I am a bit confused by the 2014 NEC with regards to VFD feeders and I'm hoping light can be shed. The feeder conductors must be sized for 125% of the DRIVE rating or 125% of the MOTOR FLA if a bypass device is used and the MOTOR FLA is higher than the drive rating. So far this makes sense. Overload protection for the MOTOR can be provided by the DRIVE and must also be provided IN THE BYPASS CIRCUIT per Article 430. The disconnecting device to the DRIVE must be sized to 115% of the DRIVE rated input current. Still good so far. But then 430.130 short circuit protection has to be based on the MOTOR per 430.52. That creates two questions for me:
1. Does this basically imply that the feeder breaker must be undersized or at least have an adjustable instantaneous that can be set down to within Table 430.52 for the motor fed by the DRIVE?
2. Since 430.52(C)(3) is referenced that would seem to imply that a combo starter with HMCP can be used to feed a VFD but 430.130(3) says "self protected combination controller shall only be permitted where specifically identified in the manufacturer's instructions for the power conversion equipment." I don't recall VFD manufacturer's listing combo starters for use with their equipment. Is this something I've missed and am I interpreting this correctly?
Thanks!
1. Does this basically imply that the feeder breaker must be undersized or at least have an adjustable instantaneous that can be set down to within Table 430.52 for the motor fed by the DRIVE?
2. Since 430.52(C)(3) is referenced that would seem to imply that a combo starter with HMCP can be used to feed a VFD but 430.130(3) says "self protected combination controller shall only be permitted where specifically identified in the manufacturer's instructions for the power conversion equipment." I don't recall VFD manufacturer's listing combo starters for use with their equipment. Is this something I've missed and am I interpreting this correctly?
Thanks!