TECMSC
Mechanical
- Oct 6, 2005
- 45
Hello All,
We are installing two new centrifugal chillers (1000T and 500T) to an existing chiller plant (2400t). Existing chillers or pumps do not have VFD's. System is Primary pumping-no primary secondary loop. During this addition we are considering adding VFD's for the new chillers.
Reliability is paramount concern although we are looking for ways to save energy as well.
I need to develop a list of pros vs cons for adding VFD's to the new chillers. Any ideas would be greatly appreciated.
My initial take is:
Pro -
1. Save energy at low load for first year (although in a year or 1 1/2 we should be at full load and not need VFD)
2. Save energy during economizer cycle since we would be reducing the load on the chiller plant i.e. be at part load on chiller plant but full load in space.
3. ??
Cons
1. VFD less reliable than other starting methods (eg reduced voltage starter)
2. VFD or VFD parts availability is questionable. VFD fails and chiller goes down; finding a VFD/VFD-part could take weeks.
3. Reliable integration of VFD w/Chiller historically has been poor.
4. Mean time to failure for VFD is shorter than other starting methods.
5 Potentially more maintenance.
6. ??
One thought is to provide both a VFD and reduced voltage starter in tandem with a xxx pole xxx throw switch to transfer power through either the VFD or alternate starter. If the VFD fails we would always be able to provide power through the alternate starter. Problem is that I'm not sure if the chiller manufacturer would warranty this type of starting option.
Comments/Thoughts greatly appreciated??
We are installing two new centrifugal chillers (1000T and 500T) to an existing chiller plant (2400t). Existing chillers or pumps do not have VFD's. System is Primary pumping-no primary secondary loop. During this addition we are considering adding VFD's for the new chillers.
Reliability is paramount concern although we are looking for ways to save energy as well.
I need to develop a list of pros vs cons for adding VFD's to the new chillers. Any ideas would be greatly appreciated.
My initial take is:
Pro -
1. Save energy at low load for first year (although in a year or 1 1/2 we should be at full load and not need VFD)
2. Save energy during economizer cycle since we would be reducing the load on the chiller plant i.e. be at part load on chiller plant but full load in space.
3. ??
Cons
1. VFD less reliable than other starting methods (eg reduced voltage starter)
2. VFD or VFD parts availability is questionable. VFD fails and chiller goes down; finding a VFD/VFD-part could take weeks.
3. Reliable integration of VFD w/Chiller historically has been poor.
4. Mean time to failure for VFD is shorter than other starting methods.
5 Potentially more maintenance.
6. ??
One thought is to provide both a VFD and reduced voltage starter in tandem with a xxx pole xxx throw switch to transfer power through either the VFD or alternate starter. If the VFD fails we would always be able to provide power through the alternate starter. Problem is that I'm not sure if the chiller manufacturer would warranty this type of starting option.
Comments/Thoughts greatly appreciated??