Hippo
Chemical
- Feb 6, 2003
- 7
Hello. I recently ran into a problem with the startup of a pair of compressors.
The vendor was asked to provide VFDs to allow the machines to turn-down to half of the design gas rate.
The vendor provided a 1000-rpm 200hp motor. On startup, the compressor could not develop the pressure needed. The reason stated was that the motor was too small. I must admit that I didn't understand this b/c we have a 200hp motor, and I know that the hp required based on the process conditions is 174hp at full load.
It turns out that the motor at turndown speed (450rpm) can only deliver 40hp and 80hp at max speed.
This is where I need a crash course (for dummies) on this limitation. Can someone briefly and simply explain this 200 hp motor can't put up 170hp?
Also, apparently we have an 1800rpm driver and a 1000rpm motor. Is this odd, or does it cause any problems?
Thanks for the help. I just want to educate myself a little on what went wrong and make sure it is avoided next time.
Mark
The vendor was asked to provide VFDs to allow the machines to turn-down to half of the design gas rate.
The vendor provided a 1000-rpm 200hp motor. On startup, the compressor could not develop the pressure needed. The reason stated was that the motor was too small. I must admit that I didn't understand this b/c we have a 200hp motor, and I know that the hp required based on the process conditions is 174hp at full load.
It turns out that the motor at turndown speed (450rpm) can only deliver 40hp and 80hp at max speed.
This is where I need a crash course (for dummies) on this limitation. Can someone briefly and simply explain this 200 hp motor can't put up 170hp?
Also, apparently we have an 1800rpm driver and a 1000rpm motor. Is this odd, or does it cause any problems?
Thanks for the help. I just want to educate myself a little on what went wrong and make sure it is avoided next time.
Mark