SteveWag
Civil/Environmental
- Dec 11, 2003
- 348
I was recently called to look at a problem at a well pump facility. Installed is an Eaton SVX9000, a TCI KMG Sine Wave Filter, 4400 feet of motor wire in buried PVC conduit and a 20 HP submersible well pump. The system has operated since 2008 without any problems. Four weeks ago it was found that the pump/VFD would not operate above about 48 hertz. That is, the drive could/would not operate at full speed either on remote or local (potentiometer). I verified that the remote input was 100%. I removed the load wiring from the VFD and operated it at 60 HZ both in remote and local. The current settings look OK, with no current limiting of speed. There is an identical unit, working, less the sine wave filter, about three feet away, with about 150 feet of motor supply wiring. I took the operator interface from that unit, inserted it into the malfunctioning VFD and downloaded the settings from the working unit with no luck. Anyone have any reason for the drive logic to limit the hertz output?
Thanks
Steve
Thanks
Steve