Shortstub,
You raise a very valid point.
If the ac line (mains) disappears, it raises several interesting considerations:
- Commutation failure of SCR's in Regen Module.
(Hopefully, module is fused.)
- If mains branch circuit fusing to Regen Module opens, then current flow path from DC bus to mains is interrupted and no damage should occur (depending upon which phase of Regen Module is in conduction at the time, and which phase fuses open.
- And of course, braking ability is lost.
Losing the 'mains' ac supply, is an argument for choosing dynamic braking as the method. The regenerative energy will keep the DC bus up ...and assuming that the power supplies of the VFD are sourced from the DC bus (as opposed to a conventional supply tied to the incoming AC power).... braking will continue until the regen energy is no longer able to keep the VFD DC bus 'pumped' up.
If the Line Regen module is chosen, and if personnel safety is a concern, one would expect that the OEM would provide some means of mechanical braking as a redundant backup (don't hold your breath on this one)...
I guess it comes down to :
~ What do you need ? and
~ what are you willing to pay ? and
~ Can you live with the compromise?