LionelHutz
Electrical
- Sep 12, 2005
- 5,354
Can anyone point me to any specific references concerning the elimination of ringing on the output of a VFD. I'm looking for some more detailed help here. Just the advise of installing an output reactor or a motor filter is no help.
I will give you an example. We had a call to a failed VFD mounted on the machine with a short run of Tech like cable, maybe 1', going to an output reactor and then another 8' of this Tech like cable going from the reactor to the motor. After installing the new unit, the voltage at the output of the VFD was measured as ringing to about 2600V peak. We removed the reactor and the ringing almost disappeared entirely so we left the installation like that.
So, reactors and filters by themselves don't solve the problem. I'm hoping a few people who have more experience with this can point to some ideas such as specific wiring techniques or grounding techniques that are known to help.
I will give you an example. We had a call to a failed VFD mounted on the machine with a short run of Tech like cable, maybe 1', going to an output reactor and then another 8' of this Tech like cable going from the reactor to the motor. After installing the new unit, the voltage at the output of the VFD was measured as ringing to about 2600V peak. We removed the reactor and the ringing almost disappeared entirely so we left the installation like that.
So, reactors and filters by themselves don't solve the problem. I'm hoping a few people who have more experience with this can point to some ideas such as specific wiring techniques or grounding techniques that are known to help.