Looking for opinions on best way to specify VFD output current rating.
As an example, if we have a 40 hp, 460 V motor with FLA = 51 and Service Factor =1.15 on a centrifugal pump, what would you consider an acceptable continuous current rating for a VFD? Do you use something like 115% of the motor FLA?
Also, is there an advantage in specifying 1 min and 3 min overload ratings for the drive? I see a wide range of standard overload current capability from the major drive suppliers, ranging from 150% for 1 minute, down to 110% for one minute.
TIA,
Dave