cokeguy
Electrical
- Jan 29, 2006
- 117
We have a 2300 gpm pump driven by a standard 100 HP induction AC motor, NEMA B design, running across the line. Because of a major piping and process change, we temporarily installed a 200 HP VFD in order to make some tests to determine the new optimum pump speed. It turns out we now need only 48 Hz to run the motor and get the more-or-less 1600 gpm we need for our application. Before installing the VFD and making the process changes, the motor was running close to the 112A FLA mark and (I assume) close to the rated 100 HP, but now with the VFD at 48 Hz the motor is taking 57 amps and the VFD display indicates a little less than 40 HP input power (it is a Saftronics GP10).
My question is, will there be a significant efficiency and thus energy consumption difference motorwise if we now change the pulley ratio to obtain the new speed and remove the VFD v.s. keeping the current pulley ratio and sticking with the VFD? Or can we expect actual motor amps and HP to be more or less the same in both cases? I would definitely prefer to return the VFD to its original "owner" (a currently unused I.D. fan), but if potential energy savings justify it I guess I could keep it as it is right now.
My question is, will there be a significant efficiency and thus energy consumption difference motorwise if we now change the pulley ratio to obtain the new speed and remove the VFD v.s. keeping the current pulley ratio and sticking with the VFD? Or can we expect actual motor amps and HP to be more or less the same in both cases? I would definitely prefer to return the VFD to its original "owner" (a currently unused I.D. fan), but if potential energy savings justify it I guess I could keep it as it is right now.