rwilsond
Firstly, get the terminology right:
“Total harmonic distortion” is defined as either harmonic voltage or current distortion factor. Therefore, the equation given for distortion factor is used to calculate Total Harmonic Current Distortion (THID) and Total Harmonic Voltage Distortion (THVD).
“Total demand distortion (TDD)” is defined as the “root-sum-square harmonic current distortion in percent of the maximum demand load current”. The equation for TDD is different to THID. The difference is that the total load current must be used in the denominator. This is the total fundamental load current resulting from all loads connected to the point of common coupling (PCC), not just the fundamental current resulting from the non-linear load(s)
The calculation of TDD is therefore a measurement of the system’s performance, not of a specific product. To calculate TDD, it is necessary to know the total fundamental load current of the system (IL).
If the total load current is unknown, a best estimate of TDD can be made by using the rated load current of the supply transformer as IL in the calculation. Using this in the calculation would assume the transformer is fully loaded.
I would say from the initial information provided, that some form of harmonic mitigation would be required, depending on the type of VFD you are using.
I did a quick calculation using just 2 x 450hp VFD's, based on our range that have built-in DC link chokes. The THvD came to 10.38% and the TDD (Total Demand Distortion) came to 17.2%. Just using these 2 drives indicated that 49% of the transformer load was harmonic load.
There are numerous methods of harmonic mitigation, I used a passive harmonic filter in the same calculation and this brought the THvD down to 2.34% and TDD to 3.12% at the transformer.
Note: these are only 'finger in the air calcs' based on the basic information provided and is assuming no other linear load and no other non-linear loads on the PCC.
The supplier of the VFD's should be able to provide some sort of calculation to simulate the their product, but as already pointed out by others-if the background harmonics are already over the limit, even supplying VFD's with zero harmonics would not meet IEEE519.
It is a system guideline not a product standard!