veritas
Electrical
- Oct 30, 2003
- 467
Suppose a VFD drive(s) is supplied from an MCC which is in turn supplied from a 480V swbd. The swbd is connected to a 1.5MVA 13.8kV/480V Dyn11 trfr. Trfr neutral has two EF relay CT’s. Trfr neutral has a 5A NER.
CT1 feeds EF1 relay: set to 500mA, 0.2s and trips the LV ACB.
CT2 feeds EF2 relay: set to 500mA, 0.5s and trips the HV breaker.
Thus EF2 acts as a back-up to EF1. Question arose as to whether the EF2 should trip BOTH the LV ACB and the HV breaker. Apparently the VFD’s are subjected to “spiking” (transient voltage spikes) when the HV CB trips and removes HV supply without the LV ACB opening.
I do not know anything about spiking really and so would like to pose the question why does spiking occur only when the HV CB opens?
Thanks.
CT1 feeds EF1 relay: set to 500mA, 0.2s and trips the LV ACB.
CT2 feeds EF2 relay: set to 500mA, 0.5s and trips the HV breaker.
Thus EF2 acts as a back-up to EF1. Question arose as to whether the EF2 should trip BOTH the LV ACB and the HV breaker. Apparently the VFD’s are subjected to “spiking” (transient voltage spikes) when the HV CB trips and removes HV supply without the LV ACB opening.
I do not know anything about spiking really and so would like to pose the question why does spiking occur only when the HV CB opens?
Thanks.