In a recent thread ( thread237-178054 ) there was some concern about influence from PWM VFDs on the three-phase system supplying DC drives. I mentioned that I was going to measure on such a system and here are the results:
The top picture shows voltage from phase A (L1) to ground. The superimposed square wave is from the VFD. It has a 2500 Hz carrier frequency and the impedance in the transformer windings *plus* the fact that the neutral is isolated result in a very high common-mode carrier residual voltage.
The DC motors have a very tight coupling between armature winding and rotor (wound directly on rotor) so the HF components are coupled to the rotor very efficiently. Once there, the charge finds its way though bearings back to ground.
Typical discharge patterns were found between shaft and frame and there were also motors that had wash-board patterns in the bearings.
We also measured other transformers with and without VFD load. One transformer with about 50 constant drives (asynchronous induction motors) had a much lower HF common mode voltage. We think (are sure) that that is because there are 50 long cables shunting the HF to ground.
So, it is not only motors connected directly to a VFD that are damaged by EMD - also (DC) motors that have been running reliably for decades can get hurt if a VFD is installed on same transformer.
Comments invited.
Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
The top picture shows voltage from phase A (L1) to ground. The superimposed square wave is from the VFD. It has a 2500 Hz carrier frequency and the impedance in the transformer windings *plus* the fact that the neutral is isolated result in a very high common-mode carrier residual voltage.
The DC motors have a very tight coupling between armature winding and rotor (wound directly on rotor) so the HF components are coupled to the rotor very efficiently. Once there, the charge finds its way though bearings back to ground.
Typical discharge patterns were found between shaft and frame and there were also motors that had wash-board patterns in the bearings.
We also measured other transformers with and without VFD load. One transformer with about 50 constant drives (asynchronous induction motors) had a much lower HF common mode voltage. We think (are sure) that that is because there are 50 long cables shunting the HF to ground.
So, it is not only motors connected directly to a VFD that are damaged by EMD - also (DC) motors that have been running reliably for decades can get hurt if a VFD is installed on same transformer.
Comments invited.
Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...