Voltage Drop for 2400V system

Status
Not open for further replies.

JCHENHI

Electrical
Nov 30, 2005
5
Dear All,

I am new to this forum and I have one question here. During our design for an airport ILS project, I find I need to calculate the voltage drop for a cable between the step-up and step-down transformer. It's about 3,170ft long and is the load is about 12amp at 2400V. My problem is that NEC Table 9 only provides cable information at 600V. How can I obtain cable info for 2400V?

Your help is highly appreciated and if there is anything wrong with my first post, just let me know.

James
 
Replies continue below

Recommended for you

An ohm is an ohm and an amp is an amp. Voltage drop in a function of amp-feet (or amp-meters) through a given impedance.
 
Thanks, davidbeach and itsmoked. But can I use the table value for 600V cable to calculate impedance of 2.4kv cable?
 
Cable manufacturer publishes impedance values or charts for MV cables. Contact Okonite, Kerite or Pirelli etc.
 
JCHENNI:

Contact the cable manufacturer and obtain the data from them.

Either:
the approx. impedance / given distance (ohm/km, ohm/mile, etc.)
or
the voltage drop per amp metre (or feet)

[red]Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon[/red]

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
 
Impedance depends on the type of cable (shielded vs. non-shielded) and physical arrangment. I agree with Ralph. The manufacturer should have impedance tables for typical installations.

Is this a series lighting circuit? Airfield systems are commonly series connected circuits, fed by a constant current transformer. In that case voltage drop may not be a significant to the design.
 
The resistance of #2 cu = .194 per 1000 ft and #2 AL = .319
per 1000 ft. An estimate of the voltage drop is

#2Cu .194 x 3.170 x 12 = 7.4 volts and for
#2al .319 x 3.174 x 12 = 12.1 volts.




 
A rough rule of thumb- One mile per 1 KV.
2.4 KV 2-1/2 miles.
YMMV depending on load.
 