noteinstein
Electrical
- May 9, 2012
- 1
Hi All,
Come across something unusual (for me at least).
Picture This;
220v 60 hz 3 Phase Supply ...
This supplies a Distribution Board from a 20amp CB with 4mm cable ...
This Dist. Board then supplies (among other circuits) from a 2 Pole 16amp Circuit Breaker a 16amp outlet on 2.5mm cable approx 25 metres in length...
Plugged into this outlet is a single phase 2.2kw compressor...
Heres the problem;
This compressor when switched on would get to 200bar and cut out on overload (it should go to 300bar easily) ...
I assumed the compressor was faulty and had it replaced ...
The new compressor would not even start without tripping its 10amp overload ...
On this compressor I measured the startup voltage/current which was 140v and 40amps respectively ...
So I took this compressor to another socket on a different DB but same main supply and it worked fine ...
I then took the old compressor to the same socket and it went to 300bar no problems ...
The only thing I can think of is Voltage Drop however the voltage at the first Socket is 217v ... hardly significant...
Plus everything else on the first DB seems fine as does anything else I plug into the first socket...
Any ideas???
Come across something unusual (for me at least).
Picture This;
220v 60 hz 3 Phase Supply ...
This supplies a Distribution Board from a 20amp CB with 4mm cable ...
This Dist. Board then supplies (among other circuits) from a 2 Pole 16amp Circuit Breaker a 16amp outlet on 2.5mm cable approx 25 metres in length...
Plugged into this outlet is a single phase 2.2kw compressor...
Heres the problem;
This compressor when switched on would get to 200bar and cut out on overload (it should go to 300bar easily) ...
I assumed the compressor was faulty and had it replaced ...
The new compressor would not even start without tripping its 10amp overload ...
On this compressor I measured the startup voltage/current which was 140v and 40amps respectively ...
So I took this compressor to another socket on a different DB but same main supply and it worked fine ...
I then took the old compressor to the same socket and it went to 300bar no problems ...
The only thing I can think of is Voltage Drop however the voltage at the first Socket is 217v ... hardly significant...
Plus everything else on the first DB seems fine as does anything else I plug into the first socket...
Any ideas???