Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations pierreick on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Voltage Insulation Level UG Cable

Status
Not open for further replies.

ePOWEReng

Electrical
Jul 15, 2003
114
Hello. What is the proper voltage insulation level for a NEC application running a 6.6kV motor? Using the utility theory, you go by the line-line voltage so we would probably need to buy 15kV cable. Right? But do the same criteria apply to a single 3-phase UG feed to a pump? Does the insulation level still need to be based on line-line do to faults?

Thanks for the help!
 
Replies continue below

Recommended for you

Yes, you should insulate based on line-to-line voltage. I believe you can buy 8 kV cable.
 
Cable insulation is based not only on the line-to-line voltage but also the thickness of the insulation is related with the clearing time of the protection system such as 100% Insulation for t<1min, 133% thickness for t<1hr and occasionally 173% for t> 1 hr.

For system voltage line-to-line >5 kV, most cabling systems are also shielded.
See the enclose reference sample:
a) Single rated: 8kV Unshielded 100% Insulation up to 90o C:
b) Double rated: 5/8 kV shielded 133%/100% insulation 105 o C:
c)Single rating: 8 kV shielded 133% insulation 105 oC
 