Hello,
I refer to a hospital istallation isolated using a 1:1 transformer. I do know know if it should be called IT or II...
During the testing phase, i touched either terminals of a "single phase" socket outlet and i did not get a shock. I used a "test" screwdriver on both terminals of the socket outlet and they both lit. So far no problem.
The only thing i did not measure was the voltage between one terminal and the earthing terminal provided for the medical equipment. Now i measure it and i find 150 volts between either of the two terminals and the earth.
In another room with a similar installation, the voltage reaches 190 V.
I have someone telling me: "i can hook a device between the 'phase' and the 'earth'". I told him you can also do the same in a normal TN instllation, you have difference of potential but no significant current will flow because of the discontinutity between the 'earth' and the second terminal. Actually the earth may be taken at a central point from the 1:1 transformer, but i am not sure.
Could you please tell me if these measurements are ok in such installations?
I refer to a hospital istallation isolated using a 1:1 transformer. I do know know if it should be called IT or II...
During the testing phase, i touched either terminals of a "single phase" socket outlet and i did not get a shock. I used a "test" screwdriver on both terminals of the socket outlet and they both lit. So far no problem.
The only thing i did not measure was the voltage between one terminal and the earthing terminal provided for the medical equipment. Now i measure it and i find 150 volts between either of the two terminals and the earth.
In another room with a similar installation, the voltage reaches 190 V.
I have someone telling me: "i can hook a device between the 'phase' and the 'earth'". I told him you can also do the same in a normal TN instllation, you have difference of potential but no significant current will flow because of the discontinutity between the 'earth' and the second terminal. Actually the earth may be taken at a central point from the 1:1 transformer, but i am not sure.
Could you please tell me if these measurements are ok in such installations?