Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

voltage regulation

Status
Not open for further replies.

bahrra

Electrical
Joined
Apr 1, 2005
Messages
9
Location
US
Where do I go to find the necessary formulas to calculate the voltage on the low side of a step down transformer? I have the impedance, the watt loss, turns ratio and the load. I can do the v=ir and calculate the voltage drop on an per unit basis but I would like to verify if I am doing it right.
 
You will have to get the voltage regulation from the manufacturers test data or published data. You can not calculate from the data you have.
 
You are basically correct. The voltage drop is the difference in source voltage magnitude and load voltage magnitude. Assume one per unit voltage at the load side and add V=I·Z vectorially to get the source voltage. You can get the transformer reactance X in pu from the impedance Z in pu and the resistance R in pu which is load loss divided by the transformer rating. X²=Z²-R²
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top