Hi all,
here's the situation; a 20MVA generator will be shutdown for 3 years at a papermill. This generator was providing all power factor correction needed by the plant. And about half of the load. (Total load is 12MW, 5.7MVar)
When the generator is down, pf at service entrance drops down to 0.87 and voltage on 13.8kV bus drops to about 13kV, and causes all kinds of problem.
Primary voltage is 22.9kV, and they use a 25kV/13.8kV transformer (16MVA), on the lowest tap (22.8kV/13.8kV). So no help here to raise the voltage.
NOTE: no pf penalities at all, they pay kw-h only!
I see three possible options:
-install a capacitor bank on 13.8kV bus: but these capacitors will be useless when the generator is put back on in three years.
-install a voltage regulator transformer(with automatic OLTC) upstream of the existing one
-change the existing transformer for a 22.9kV/13.8 kV with automatic OLTC
I would like to have your opinions about this project.
Thanks!
here's the situation; a 20MVA generator will be shutdown for 3 years at a papermill. This generator was providing all power factor correction needed by the plant. And about half of the load. (Total load is 12MW, 5.7MVar)
When the generator is down, pf at service entrance drops down to 0.87 and voltage on 13.8kV bus drops to about 13kV, and causes all kinds of problem.
Primary voltage is 22.9kV, and they use a 25kV/13.8kV transformer (16MVA), on the lowest tap (22.8kV/13.8kV). So no help here to raise the voltage.
NOTE: no pf penalities at all, they pay kw-h only!
I see three possible options:
-install a capacitor bank on 13.8kV bus: but these capacitors will be useless when the generator is put back on in three years.
-install a voltage regulator transformer(with automatic OLTC) upstream of the existing one
-change the existing transformer for a 22.9kV/13.8 kV with automatic OLTC
I would like to have your opinions about this project.