How is it possible to have such small size voltage transformer within 220kV GIS?
If we consider the ratio--220kV/110V and the turns that needs to be wound 2000--it is huge--still how do manufacturers manage to put it in such a small enclosure.

 

The main reason is that the GIS is enclosed in SF6 and dielectric clearance is significantly reduced compared with air. The AIS VT must have a large bushing to maintain the clearance between the energized part on top (xx kV) and the base tank at ground potential (V=0).

See the illustration below.

VT_GIS_vs_AIS_hy0zvq.jpg
 