Voltage transformer in GIS

Status
Not open for further replies.

ravindranathan

Electrical
Sep 30, 2006
35
How is it possible to have such small size voltage transformer within 220kV GIS?
If we consider the ratio--220kV/110V and the turns that needs to be wound 2000--it is huge--still how do manufacturers manage to put it in such a small enclosure.

 
Replies continue below

Recommended for you


The main reason is that the GIS is enclosed in SF6 and dielectric clearance is significantly reduced compared with air. The AIS VT must have a large bushing to maintain the clearance between the energized part on top (xx kV) and the base tank at ground potential (V=0).

See the illustration below.

VT_GIS_vs_AIS_hy0zvq.jpg
 