Volume change restraint forces at precast shear walls in Garage

Status
Not open for further replies.

kimwakes

Structural
Jun 4, 2007
1
Any tips on accomodating volume change at connx between precast double tee flange and precast shearwall (parallel to tee stems) while still transfering diaphragm shear to the wall?

The colinear shearwalls in this 6 level parking facility are 120 ft apart...and, due to creep, shrinkage and temperature, I anticipate about 1/2" shortening at each end of the DT in the unrestrained condition. If the DTs are considered restrained, I anticipate about 3/16" shortening at each end of the DT, but the restraint force is excessive.

Any suggestions are appreciated.

 
Replies continue below

Recommended for you

Welded steel straps at the ends and midpoint of the double tees flanges to embeded plates in the shear wall. The small length of strap between the connecting welds will rotate and flex to match the 0.08% length change. More straps can be used if wanted.
 