Hi All
I have read several posts on here about sizing of VFD supply conductors... most of them deliberating the technical merits of the rule in the NEC stating the conductors need to be sized to the VFD, not the motor, with a 20% allowance (or similar)
I am in Australia and we follow IEC regulations, as far as I know there is no such requirement.
I am working for a customer who is a switchboard builder and is trying to save every $ they can. In addition, the designer has oversized the VFDs (in some cases, by 50%). So the switchboard builder does not want to size cables to the drive, they want to size to the motor (with an allowance for THD, drive and motor efficiencies, etc). This includes the line side protection as well as the cable.
So my question is, what is the technical feasibility of this approach. You guys have talked a lot about the NEC requirement, but I can't find where anyone takes the requirement apart and tries to determine WHY it exists.
All I can think of is the requirement to allow for charging the DC bus, but with soft charging circuits, this is not so much of a problem.
Can anyone think of why it would be technically incorrect to size line side cables and breakers to the motor size and not the drive. Assuming the motor size will never change.
Thanks.
I have read several posts on here about sizing of VFD supply conductors... most of them deliberating the technical merits of the rule in the NEC stating the conductors need to be sized to the VFD, not the motor, with a 20% allowance (or similar)
I am in Australia and we follow IEC regulations, as far as I know there is no such requirement.
I am working for a customer who is a switchboard builder and is trying to save every $ they can. In addition, the designer has oversized the VFDs (in some cases, by 50%). So the switchboard builder does not want to size cables to the drive, they want to size to the motor (with an allowance for THD, drive and motor efficiencies, etc). This includes the line side protection as well as the cable.
So my question is, what is the technical feasibility of this approach. You guys have talked a lot about the NEC requirement, but I can't find where anyone takes the requirement apart and tries to determine WHY it exists.
All I can think of is the requirement to allow for charging the DC bus, but with soft charging circuits, this is not so much of a problem.
Can anyone think of why it would be technically incorrect to size line side cables and breakers to the motor size and not the drive. Assuming the motor size will never change.