Kiribanda
Electrical
- May 6, 2003
- 698
Hello all,
We have got an issue about a set of VTs.
A MV metal clad switchgear is supplied by a 13.8-4.16 kV Dyn1 power transformer. A set of PT (or VT) with the ratio 4.2 kV-120V is installed on the 4.16 kV STAR side to feed secondary line to line bus voltages for the metering and relay (ANSI # 27, 47, 59, 60) panel. The connection of the PT set is OPEN DELTA-OPEN DELTA corner grounded (commonly known as V-V grounded).
What will be the Line to Line voltages seen by the above mentioned relays on the 120 V side, and how to calculate them,
1)When one 13.8 kV phase is open due to a fuse blown condition of the primary side of the Dyn1 power transformer?
2)When one phase of the primary side of the VT is open due to VT primary side fuse blown condition?
3)When one phase of the secondary side of the VT is open due to VT secondary side fuse blown condition?
Most of the relay manuals (SEL, BASLER etc) discuss about the corresponding reflected voltages on the 120 V side with YNyn connected VT sets (e.g. generating stations where ANSI# 51V relays are fed).
Thanks in advance!
We have got an issue about a set of VTs.
A MV metal clad switchgear is supplied by a 13.8-4.16 kV Dyn1 power transformer. A set of PT (or VT) with the ratio 4.2 kV-120V is installed on the 4.16 kV STAR side to feed secondary line to line bus voltages for the metering and relay (ANSI # 27, 47, 59, 60) panel. The connection of the PT set is OPEN DELTA-OPEN DELTA corner grounded (commonly known as V-V grounded).
What will be the Line to Line voltages seen by the above mentioned relays on the 120 V side, and how to calculate them,
1)When one 13.8 kV phase is open due to a fuse blown condition of the primary side of the Dyn1 power transformer?
2)When one phase of the primary side of the VT is open due to VT primary side fuse blown condition?
3)When one phase of the secondary side of the VT is open due to VT secondary side fuse blown condition?
Most of the relay manuals (SEL, BASLER etc) discuss about the corresponding reflected voltages on the 120 V side with YNyn connected VT sets (e.g. generating stations where ANSI# 51V relays are fed).
Thanks in advance!