mikelangel78
Electrical
- Mar 5, 2015
- 26
Hello everyone,
I'm testing a 220kV Voltage Transformer with a CPC100 Omicron device.
One of the test that i've to perform is the phase checking. I've a three-phase VT of a bank of three single phase VTs.
I'll do a primary injection and measure the voltage between phases and neutral in the secondary side, at a marshalling box. These three-phase VT have a tertiary winding (broken delta configuration), and the voltage between the neutral and phase of this winding must be measure.
I've made some calculations (see the attached file) and i'll be very happy if someone could confirm my calculations.
Thank you in advanced,