VT/PT Secondary as point of isolation

Status
Not open for further replies.

dfdt

Electrical
Sep 10, 2002
118
0
0
AU
Most of us know that during planned outage of primary plant/equipment its customary to isolate all possible points/sources of energisation and secondary of voltage transformer being one of them. Our issue is that we also check for the status of PT/VT mcb as one of the condition required to close Earth switch (presence of under/no voltage provided mcb is closed. Hence we are in quandary i.e. continue with out practice of opening & tagging the mcb or let it remain closed so the earth switch interlock is reliable.
Any comments or suggestions?
 
Replies continue below

Recommended for you

Check your primary voltage with a Modiewark.
image_p5me7w.png

image_dkt4vy.png

Link

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
Just check on the VT side of the MCB. Opened or closed ceases to matter.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Voltage tester/sensors may be alright for medium voltages but can these be used for voltages 220kV and above?
 
Raghu - In our case Primary side is not isolated as its hard on connection to Air Insulated Busbar (outdoor switchyard)
 