Walk-in cooler / refrigerator ventilation? 1

Status
Not open for further replies.

m2e

Mechanical
Jun 28, 2006
91
In a food and beverage plant, they have a big room (300' x 300' x 50') to store the finished products. It's a refrigerated room but there is no ventilation.

What's the requirement for ventilation for this type of room? I can't find it in ASHRAE 62.1.

Thanks.
 
Replies continue below

Recommended for you

62.1-2013 addendum l, added a row for freezers and refrigerated spaces. How many people do you expect to be working in there? How long will they remain in there? Additional ventilation is required if combustion, like propane forklifts are also in there.

knowledge is power
 
Thank you. Forklifts are electric so that's not a problem. There may be 2 people working, and I would expect they go in and out fork-lifting the pallets out the space.
 
Ashrae has 10 cfm/person, and no requirement for area, which seems a little light for that sized space, but on the otherhand, refrigerated makeup air can be expensive.