Wall Mounted Equipment

Zoletres

Mechanical
Jun 30, 2024
2
I had a question about the h and z values when using ASCE 7 Eq 13.3-1 for wall mounted equipment. I'm used to seeing this equation for floor mounted equipment, essentially on a pad. Usually here h is the height of the equipment and z is 0. Would any of the values I have in the attached picture be the proper value for h and z?
 

Attachments

  • Wall Anchor.png
    Wall Anchor.png
    296.3 KB · Views: 11
Replies continue below

Recommended for you

h is the height of the roof of the overall building. Z is the height of the component anchorage. Both values should be measured from the same reference level (ground)
 
Sometimes a picture is worth a thousand words. The following sketch explains 0.4SDS(1 + 2 z/h)

1734699150589.png
 

Attachments

  • FEMA nonstructural components .pdf
    3.9 MB · Views: 4