Mr Che said:
2. How can a transformer rated 240V about 500 VA or greater, or 220V about 750VA or greater; which is <1/3 or <1/2 of motor (>1.85kW at 60Hz) be suitable for the job?
Auto-transformers 101.
With a 120:48 Volt auto-transformer Boosting a 10 Amp motor current, only the 24 Volt winding sees the ten Amp motor current.
10 Amps times 48 Volts = 480 VA.
But the 10 Amps was a guesstimate. At 1385 RPM your slip is 115 RPM.
115 RPM is a relatively high slip and high slip motors tend to have more losses, so a typical current estimate tends to be low.
Thus I opted to recommend transformers a little on the high side.
This formula is for step-up applications only.
For step down applications, the transformer primary current must be added to the secondary current to determine VA rating.
Dropping from 450 Volts to 264 Volts will be extremely difficult to do with standard transformer voltages.
But don't panic; 450 Volts line to line will have a line to neutral voltage of 260 Volts.
Capacitors may be a problem.
If the run capacitor is carrying part of the motor current, it may be causing part of the overheating.
Typically, the run capacitor shifts the phase angle of the current applied to the start winding so that the start winding may assist the main winding by supplying added torque.
With a higher frequency, the capacitive reactance will be lower and this may be causing the start winding to take a disproportionate share of the load.
The solution; A lessor rated run capacitor.
Given the actual motor current, for auto-transformer step up I use the equation:
Motor current x Transformer secondary voltage = VA transformer capacity.
10 Amps x 48 Volts boost = 480 VA.
Note: If 10 Amps is the actual motor current, I would use a 500 VA transformer.
Given that the 10 Amps is a guesstimate, I recommended the next larger size transformer eg: 750 VA.
By the way, over the years I have several times done successful 50/60 Hz and 60/50 Hz conversions.
I have converted 50 Hz motors imported into Canada's 60 Hz grid and I have converted 60 Hz motors exported to 50 Hz grids.