dodson
Structural
- Dec 1, 2006
- 11
I have a project with wide flange girders, wide flange joists at ~8' oc supporting a 5" deck with slab. For the joist to girder connections I have a standard double angle bolted connection. The fabricator used short slotted holes in all of the angles. He used washers on the nut side of the bolts but not the head side. He is using a traditional bolt with a smaller head instead of the twist off bolts with larger heads causing part of the short slotted hole to be exposed. The inspector is telling him that per Section 6.1.12 in 16.2 of AISC, that the entire hole must be covered up, which would required him to remove and re-install every bolt on the job. My question is, since this connection is strictly in bearing, is dishing really a concern?