exzavior7
Mechanical
- May 9, 2013
- 1
We have 3 WAHP's running to cool/heat our building. The whole building is about 3 years old. We had some problems over the winter with one of heat pumps (6-ton Trane GEHE) locking out on high pressure, the fan would continue to run and compressore would shut down, particularly when OA temps dropped below -10F. After checking airflow (appears normal), checking waterflow (appears normal when the heat pump is actually working), and inlet/outlet water temps were fine (37F at the lowest outlet, and system has 35% glycol). The strainer was full of flux, tons of flux. I was concerned with all the excess flux that the heat exchanger might be gummed/plugged up. But the heat pumped worked when OA temps were above -10F, in fact the compressor would kick back on automatically when the OA temps rose above -10F.
All of that is to say, I kept coming to the conclusion that the heat pump was really locking out because of too low MA temp from the OA being so cold. While the other smaller heat pumps worked great all the time (they have very minimal OA). My math calc'd a MA temp of around 52F entering the bad heat pump when the OA temp was at -10F. Which made sense if there's a low-limit lock-out on these heat pumps (<55F). Unfortunately for me but great for the clients using the building, we didn't have a another -10F day/week for the rest of the winter, so everything worked again and I wasn't able to test my theory and close the OA off to that heat pump.
Now its the hot summer (99F yesterday) and that same heat pump is locking out on high pressure. I haven't been around to know all of the details (still getting the details for the maintenance worker there), but I do know its high pressure lock out. Water temps are good (not too hot, 52F). Airflow is good. The fan continues to run while the compressor is shut down. I do not know if/when it starts back up, if it ever does, I don't know yet.
Any ideas to why the heat pump is locking out on high pressure at the extreme end of the temps? I have more that enough capacity in my bore field to handle the peak loads of heating and cooling.
Is it just a coincendence that it locks out during these peak temps? Bad pressure switch? Plugged heat exchanger? Over charged refrigerant (I'm least familiar over charge symptoms)? All these problems coincide with the high pressure lock out in both heating and cooling seasons, but I'm just not sure where to go right now. Thanks -
All of that is to say, I kept coming to the conclusion that the heat pump was really locking out because of too low MA temp from the OA being so cold. While the other smaller heat pumps worked great all the time (they have very minimal OA). My math calc'd a MA temp of around 52F entering the bad heat pump when the OA temp was at -10F. Which made sense if there's a low-limit lock-out on these heat pumps (<55F). Unfortunately for me but great for the clients using the building, we didn't have a another -10F day/week for the rest of the winter, so everything worked again and I wasn't able to test my theory and close the OA off to that heat pump.
Now its the hot summer (99F yesterday) and that same heat pump is locking out on high pressure. I haven't been around to know all of the details (still getting the details for the maintenance worker there), but I do know its high pressure lock out. Water temps are good (not too hot, 52F). Airflow is good. The fan continues to run while the compressor is shut down. I do not know if/when it starts back up, if it ever does, I don't know yet.
Any ideas to why the heat pump is locking out on high pressure at the extreme end of the temps? I have more that enough capacity in my bore field to handle the peak loads of heating and cooling.
Is it just a coincendence that it locks out during these peak temps? Bad pressure switch? Plugged heat exchanger? Over charged refrigerant (I'm least familiar over charge symptoms)? All these problems coincide with the high pressure lock out in both heating and cooling seasons, but I'm just not sure where to go right now. Thanks -