Waramanga
Mechanical
- Jun 21, 2009
- 170
Hi Guys,
I am looking at the CIBSE code W for flow tolerances. if my coil needs a flow of 0.1574XXXX l/s and I have a tolerance of +- 10%, what decimal point goes in the coil schedules? I am thinking at if the flow needs to be within 10% then I need the third decimal place, ie 0.157 l/s, because +10% would be 0.172 and -10% would be 0.142 and without the third decimal place you could be anywhere between 0.140 and 0.149. Am I correct in concluding that if a accuracy of 10% is required, three significant numbers are needed? Does this make sense in that Kv numbers on balancing valves only go to three significant figures?
Would someone be nice enough to confirm or explode my understanding?
Thank you
I am looking at the CIBSE code W for flow tolerances. if my coil needs a flow of 0.1574XXXX l/s and I have a tolerance of +- 10%, what decimal point goes in the coil schedules? I am thinking at if the flow needs to be within 10% then I need the third decimal place, ie 0.157 l/s, because +10% would be 0.172 and -10% would be 0.142 and without the third decimal place you could be anywhere between 0.140 and 0.149. Am I correct in concluding that if a accuracy of 10% is required, three significant numbers are needed? Does this make sense in that Kv numbers on balancing valves only go to three significant figures?