We regularely take oil samples from our clients transformers in order to analyse their dissolved gas content and oil properties.
Sometimes (and it happens a couple of times in the last few months), we see a sudden change in water content (for example from 10 ppm to about 50 ppm a year later), without any major difference in other parameters (dielectric strength, etc). When it happens, we go back and take another sample in order to confirm the increase and, most of the times, it's much lower and thus closer to the last year sample.
Of course, I understand that a sample can be contaminated by water or humidity (to minimize this, we take at least 1 to 2 liters of oil and operate the valve in order to remove all the trapped water before taking the sample). This would be the main reason for a higher water content.
But is it possible that the higher water content be the real value? Would it be possible that an oil sample taken from a transformer with an global average water content of 50 ppm be at 10 or 15 ppm? I was not able to find much informations about how the dissolved water content is distributed inside a transformer. Can some oil water content be significantly higher or lower than the average?
Sometimes (and it happens a couple of times in the last few months), we see a sudden change in water content (for example from 10 ppm to about 50 ppm a year later), without any major difference in other parameters (dielectric strength, etc). When it happens, we go back and take another sample in order to confirm the increase and, most of the times, it's much lower and thus closer to the last year sample.
Of course, I understand that a sample can be contaminated by water or humidity (to minimize this, we take at least 1 to 2 liters of oil and operate the valve in order to remove all the trapped water before taking the sample). This would be the main reason for a higher water content.
But is it possible that the higher water content be the real value? Would it be possible that an oil sample taken from a transformer with an global average water content of 50 ppm be at 10 or 15 ppm? I was not able to find much informations about how the dissolved water content is distributed inside a transformer. Can some oil water content be significantly higher or lower than the average?