rawelk
Industrial
- Apr 11, 2002
- 72
We use a four cartridge stainless steel filter cartridge housing equipped with Parker T23R10A, 5 micron, wound polypropylene filters. These filter cartridges are 10" long x 2-1/2" OD x 1.0" ID, and rated for 4 GPM max. at 140°F max.
Chilled water at 55°F nominal comes into the filter from the process pump manifold (pump outlet pressure approximately 85 PSI), and returns to the chilled water tank (that is, in a side stream configuration) where return water flow can be observed. Our chilled water is used to cool rolls used in a plastics extrusion process, and also feeds several temperature control units used for mold temperature control.
The only unusual plumbing is I've tapped off from the filter outlet, and side-stream part of this flow over to an electrical enclosure cabinet cooler (a Kooltronics model KNHE28 heat exchanger installed late last summer), and then dump that back into the tank.
This housing has a pressure gauge mounted on the lid to show filter housing back pressure, and ranges from approximately 36 to 38 PSI after filter replacement, and reaches a maximum of approximately 10 to 12 PSI below pump pressure when fully blocked.
My question isn't one about whether these filters are a good match for the application (although I wouldn't mind any opinions in this area), but rather what are regarded as good strategies for determining when to schedule element replacement.
My opinion is filter replacement should be done once back pressure has reached approximately 90% of the "fully blocked" back pressure value (in this case, "fully blocked" ranges from 75 to 77 PSI, so I would change at 70 to 72 PSI) because not much more filter capacity remains, and flow is starting to drop off.
Another opinion holds that replacement is only necessary once return flow is visibly quite a bit less forceful.
It seems to me that replacement at the 90% blocked point serves, over time, to remove more solids from the water system than waiting for nearly complete blockage.
Another point - for one span of time over these daily observations I allowed filters to remain totally blocked for more than a week, and noticed back pressure increasing and decreasing out of step with pump pressure (for instance, 69, 74, 72, 69, 77, and 75 PSI with pump pressure ranging from 84 to 88 PSI over this time, and not necessarily higher on days with high back pressure). I am not certain, but speculate that filtered debris was breaking free from the filter ID, and re-entering the tank.
Since I'm using this flow for cabinet cooling, waiting for severe flow reduction causes cabinet temperatures to rise. This isn't a big deal now because ambient temperatures have been consistently below 80°F since mid-September, 2008, but will become more important as summer 2009 comes upon us.
I'm wondering if there are any "rules-of-thumb", or accepted practices, and will appreciate any commentary on this question.
Chilled water at 55°F nominal comes into the filter from the process pump manifold (pump outlet pressure approximately 85 PSI), and returns to the chilled water tank (that is, in a side stream configuration) where return water flow can be observed. Our chilled water is used to cool rolls used in a plastics extrusion process, and also feeds several temperature control units used for mold temperature control.
The only unusual plumbing is I've tapped off from the filter outlet, and side-stream part of this flow over to an electrical enclosure cabinet cooler (a Kooltronics model KNHE28 heat exchanger installed late last summer), and then dump that back into the tank.
This housing has a pressure gauge mounted on the lid to show filter housing back pressure, and ranges from approximately 36 to 38 PSI after filter replacement, and reaches a maximum of approximately 10 to 12 PSI below pump pressure when fully blocked.
My question isn't one about whether these filters are a good match for the application (although I wouldn't mind any opinions in this area), but rather what are regarded as good strategies for determining when to schedule element replacement.
My opinion is filter replacement should be done once back pressure has reached approximately 90% of the "fully blocked" back pressure value (in this case, "fully blocked" ranges from 75 to 77 PSI, so I would change at 70 to 72 PSI) because not much more filter capacity remains, and flow is starting to drop off.
Another opinion holds that replacement is only necessary once return flow is visibly quite a bit less forceful.
It seems to me that replacement at the 90% blocked point serves, over time, to remove more solids from the water system than waiting for nearly complete blockage.
Another point - for one span of time over these daily observations I allowed filters to remain totally blocked for more than a week, and noticed back pressure increasing and decreasing out of step with pump pressure (for instance, 69, 74, 72, 69, 77, and 75 PSI with pump pressure ranging from 84 to 88 PSI over this time, and not necessarily higher on days with high back pressure). I am not certain, but speculate that filtered debris was breaking free from the filter ID, and re-entering the tank.
Since I'm using this flow for cabinet cooling, waiting for severe flow reduction causes cabinet temperatures to rise. This isn't a big deal now because ambient temperatures have been consistently below 80°F since mid-September, 2008, but will become more important as summer 2009 comes upon us.
I'm wondering if there are any "rules-of-thumb", or accepted practices, and will appreciate any commentary on this question.