Buildtech2
Mechanical
- Mar 6, 2012
- 158
In chemical warehouse where hazardous chemicals will be stored in a racking system.The warehouse height is 7.5 m and total area is 2025 sqm. As per MSDS sheets, water foam sprinkler system to be used but this facility can be classified as Extra hazard, group-1 as per NFPA. As per manufacturers instructions and NFPA 16, the k factor shall be 3.0 gpm/psi (Tyco Model B-1) with minimum discharge pressure not less than 30 psi and I believe that water foam density shall be 0.16 gpm/sqft for the foam system. Now my question is as follows.
What density to be considered in hydraulic calculations?
If I use density as 0.16 gpm/sqft,I cannot use 2500 sqft as sprinkler area of operation and 100 sqft as sprinkler area coverage. In order to consider this facility as an extra hazard, I must use 0.3 gpm/sqft and 100 sqft as sprinkler coverage area.
It would be highly appreciated if anybody can guide me on this.
What density to be considered in hydraulic calculations?
If I use density as 0.16 gpm/sqft,I cannot use 2500 sqft as sprinkler area of operation and 100 sqft as sprinkler area coverage. In order to consider this facility as an extra hazard, I must use 0.3 gpm/sqft and 100 sqft as sprinkler coverage area.
It would be highly appreciated if anybody can guide me on this.