MacMcMacmac
Aerospace
- Sep 8, 2010
- 56
Hello. I am currently in the middle of a repair on a pair of three-phase water rheostats. They are used as a soft-start for a pair of 1300hp, 2300V wound-rotor motors which drive two separate stages of a 2MW exhauster. As a routine maintenance task, I recently removed 4 mild steel tube bundles from within the rheostat tanks which provide cooling for the rheostats. Although they are not very old, they have suffered from quite a bit of corrosion, mainly due to infrequent use, as well as being a local low spot in the cooling loop, which has led to a lot of sediment build up. After 4 days of cleaning and reassembly, pressure testing of the coolers has revealed leaks at the tube to end plate interface. Each tube was individually tig welded to the plate, but corrosion of the plate itself has led to leaking underneath some of the welds, as far as I can determine. Re-welding the coolers will be very time consuming, and will not solve the original problem of corrosion in the tube nest. As the tubes contain cooling tower water treated with various microbicidal and anti-corrosion chemicals, and the rheostats themselves are filled with distilled water lightly dosed with sodium carbonate, it is imperative that the coolers do not leak at all.
I have been trying to come up with an alternate solution. One idea is to build up a manifold of soldered copper pipe, probably 2" diameter, in the shape of a ladder, or two ladders back to back. The pipes would be several times larger in diameter than the individual 1" tubes in the nest, which would greatly reduce the tendency to foul, since they would not rust inside, and the velocity of the water through them would be greater than through the smaller but more numerous steel tubes. They would also be far more thermally conductive than the mild steel tubes currently in use. I am concerned with the fact that dissimilar metals would be immersed inside a large steel tank, but since it is filled with distilled water, would this be an issue? The tube bundles themselves were pristine on the outside after being submerged in the rheostat tanks for over 5 years. I measured the resistance of the water to approximately 500K Ohms. I check the specific gravity of the water almost weekly and it does not vary.
Another solution I have considered is to cool the rheostat water directly by pumping it from the tank, through a fan cooled water to air heat exchanger, then back into the rheostat tank. There are two 1" valves on either side of the tanks for draining. I was thinking I could pump from one side, put the water through a heat exchanger, then put it back in through the other side. The big bonus would be the elimination of the need for process cooling water, and the risk of it entering the rheostat due to a leak. What I am concerned about here is the fact that I may be introducing contaminants in the form or metal ions (?) from the pump and piping into the distilled water, although there is some rust already in the water which has fallen in from parts of the tank cover. I am also concerned if water turbulence in the tank would upset the operation of the rheostat itself.
A few other quick questions:
Is there a way to calculate how much heat is being generated within the rheostat based on voltage/amperage conditions while the rheostat is not fully closed? We sometimes have to operate the rheostat at partial load when we use the 2MW exhauster as a soft start for a 5MW exhauster/compressor through a suction turbine attached to the rear of the 5MW machine. It may remain in the partially closed position for several minutes.
Does temperature affect the resistance value of the water?
Any opinions you can offer would be greatly appreciated.
I realize this is old technology, but it was installed in the late 40's or early 50's and it works extremely well. Frankly, I am amazed that you can run 2300V through a steel tank filled with water and not electrocute everyone within 20 feet of the things, but obviously I am missing out on some basic theory of how they operate.
I have been trying to come up with an alternate solution. One idea is to build up a manifold of soldered copper pipe, probably 2" diameter, in the shape of a ladder, or two ladders back to back. The pipes would be several times larger in diameter than the individual 1" tubes in the nest, which would greatly reduce the tendency to foul, since they would not rust inside, and the velocity of the water through them would be greater than through the smaller but more numerous steel tubes. They would also be far more thermally conductive than the mild steel tubes currently in use. I am concerned with the fact that dissimilar metals would be immersed inside a large steel tank, but since it is filled with distilled water, would this be an issue? The tube bundles themselves were pristine on the outside after being submerged in the rheostat tanks for over 5 years. I measured the resistance of the water to approximately 500K Ohms. I check the specific gravity of the water almost weekly and it does not vary.
Another solution I have considered is to cool the rheostat water directly by pumping it from the tank, through a fan cooled water to air heat exchanger, then back into the rheostat tank. There are two 1" valves on either side of the tanks for draining. I was thinking I could pump from one side, put the water through a heat exchanger, then put it back in through the other side. The big bonus would be the elimination of the need for process cooling water, and the risk of it entering the rheostat due to a leak. What I am concerned about here is the fact that I may be introducing contaminants in the form or metal ions (?) from the pump and piping into the distilled water, although there is some rust already in the water which has fallen in from parts of the tank cover. I am also concerned if water turbulence in the tank would upset the operation of the rheostat itself.
A few other quick questions:
Is there a way to calculate how much heat is being generated within the rheostat based on voltage/amperage conditions while the rheostat is not fully closed? We sometimes have to operate the rheostat at partial load when we use the 2MW exhauster as a soft start for a 5MW exhauster/compressor through a suction turbine attached to the rear of the 5MW machine. It may remain in the partially closed position for several minutes.
Does temperature affect the resistance value of the water?
Any opinions you can offer would be greatly appreciated.
I realize this is old technology, but it was installed in the late 40's or early 50's and it works extremely well. Frankly, I am amazed that you can run 2300V through a steel tank filled with water and not electrocute everyone within 20 feet of the things, but obviously I am missing out on some basic theory of how they operate.