Regardless of the gases in the flare system, the loop seal shown in your PID is essentially a drain which you need because the bottom plate of the flare is below the inlet nozzle and can collect atmospheric moisture as well as liquids from the line (as suggested by MortenA). The 4.6 m depth is needed to prevent the external seal from blowing when there is a high back pressure in the stack. The water supply is needed because you cannot rely on having any liquids to seal the loop provided by the process or from rainwater.
If you put the stack sealing plate immediately at the inlet nozzle and slope it back, making a Bend rather than a Tee, you could drain the stack directly back into the incoming line from the KO drum and avoid the use of the drain shown in the PID. (line needs to slope back as well as suggested by note 3)
Regards
David