MechGuy22

Mechanical
Jun 8, 2010
51
Im looking for some ideas on what would cause a WSHP compressor to fail pre-maturely & repeatedly. I know the problem could be air flow or water flow, but these systems are actually ductless so I am all but eliminating the possibility of airflow.

Any ideas/references would be helpful.
 
Replies continue below

Recommended for you

Is this multiple WSHP's on one CW loop? The units should trip out if the water or airside gets too far out of whack, but, are the water and air within normal temperature bounds?

The published normal life of any compressor is based on an operational diversity - some assumed start stop - # of cycles. If they are being run constantly, they will die younger (sooner).

Alternatively, the brand/model year could be junk - ask the service tech, hint at falling for an upsell and he might tell you. Google your model number for forum comments.
 
Fouling of the water side of the coil acting as condenser and continuous operation at high discharge pressure.

Fouling of the water side of the coil acting as evaporator causing no superheat or incomplete evaporation and slugging.

Flooded starts.

Is this one compressor that keeps failing, or a problem with many compressors in similar units?

 
ductless doesn't mean there is No air flow passing the unit, if there is no air flow then what this unit does?
 